Next I will be looking to see if I have any issues with LP Gas system. The stove, furnace and fridge appear to be working fine. I have not tested the water heater yet as I have it in the winterized mode.
From what I can tell, I need to put a pressure guage near the regulator, turn on the gas at the tank, then note the pressure, turn the gas off and hope the pressure does not drop. I should have done the leak down test first, before I tested the appliances, but I didn't know about it then and still made it out alive.
Could someone suggest a guage? I think I want to put it on the 4-port tee, maybe on the 1/4" inverted flare fitting. As someone suggested, I may want to rotate the T ports down to where the 1/4" port is pointing down.
Thanks!
* This post was
edited 03/28/23 02:11pm by SCADAMAN29325 *
THANKS! Phil and LuAnn
1st timers, brought it home 2022-10-19.
1994 Fleetwood Jamboree Rallye
M-T31-Ford-460, 1994 Ford E350
I may not know what I am doing, but I am having fun doing it!
|
enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile


|
Gauge should be on the line beyond the regulator. My old Itasca had a gauge installed in the refer outside access.
Soapy water is beast for the high-pressure side.
Bud
USAF Retired
Pace Arrow
2003 Chev Ice Road Tracker
|
wolfe10

Florida

Senior Member

Joined: 10/08/2000

View Profile

Offline
|
A little difficult to tell from the picture, but it appears the regulator vent in in the long axis of the regulator. This is NOT the correct PN for a horizontal installation.
The vent (quarter sized screen) needs to POINT DOWN.
The place you bought it should have asked if it would be installed horizontally or vertically.
Yes, this is a safety issue.
* This post was
edited 01/13/23 08:38am by wolfe10 *
Brett Wolfe
Ex: 2003 Alpine 38'FDDS
Ex: 1997 Safari 35'
Ex: 1993 Foretravel U240
Diesel RV Club:http://www.dieselrvclub.org/
|
Thomas/NH

Exeter, NH

Senior Member

Joined: 03/22/2009

View Profile


Good Sam RV Club Member
Offline
|
The operating pressure for liquid petroleum or LP gas appliance is 10" - 11" of water column. Going above that pressure you can rupture the pressure regulators in the appliances. I shut off the gas valves and test the lines at 5 PSI for 20 min. I'm a licensed gas technician.
|
ernie1

Sacramento,California,USA

Senior Member

Joined: 02/10/2004

View Profile


Good Sam RV Club Member
|
Thomas/NH- What does one do at high altitude when gas appliances don't want to operate? Is it ok to set the regulator for a higher pressure?
|
|
enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile


|
11-inch column of water I believe translate to somewhere 1/2 PSI.
Anybody know for sure?
|
Thomas/NH

Exeter, NH

Senior Member

Joined: 03/22/2009

View Profile


Good Sam RV Club Member
Offline
|
Running LP at high altitude is more a problem of getting the liquid in the tanks to flash-up to a gas. The regulator will do it's best to compensate, but if there is little pressure in the tank it won't work. Readjust the pressure is a bad idea for when you return to lower levels. Short-term heating the tank would work, long-term (stationary appliances) changing the orifices is what we do. You probably wouldn't like the way I heat the tanks; I use a torch (yes and open flame on the tank) and no I haven't blown up yet (I've been doing this job for 54 years). I guess you need to know how and where to put the flame.
Yup, 12" WC is pretty close to a half pound, but that's a real pour way of measuring it.
|
GottaRunGottaCamp

East of Atlanta, Ga.

Senior Member

Joined: 11/26/2006

View Profile

Offline
|
enblethen wrote: 11-inch column of water I believe translate to somewhere 1/2 PSI.
Anybody know for sure?
There is 28 in. (27.68 to be exact) of water column in 1 PSI.
2016 F350
2019 Heartland Torque TQ-371
|
enblethen

Moses Lake, WA

Senior Member

Joined: 01/05/2005

View Profile


|
My memory serves me that the gauge on my old rig was 0 to 1.5 psi.
Had to turn off LP tank and look to see how much PSI dropped in 2 hours. Any drop was bad.
|
SCADAMAN29325

Clinton, SC

Full Member

Joined: 10/18/2022

View Profile

Offline
|
wolfe10 wrote:
A little difficult to tell from the picture, but it appears the regulator vent in in the long axis of the regulator. This is NOT the correct PN for a horizontal installation.
The vent (quarter sized screen) needs to POINT DOWN.
The place you bought it should have asked if it would be installed horizontally or vertically.
Yes, this is a safety issue.
I found a pic of the old installation, so I need to rotate the regulator like this, correct? BTW, I did this (and learned that the input end has left hand threads). I don't want anyone else taking credit for my screw ups!
I think someone mentioned this before and I thought they were talking about the 4-port T.
|
|