Great camping trip last week, but woke up cold every night. LOL
1st night- We camped off a fire service road until the state parks opened the next day. The battery died sometime in the night. No problem. Borrowed my father in law's generator.
2nd night- On shore power. Propane bottle empty. No problem. Switched tank.
3rd night- Problem! On shore power, gas to stove is working. Blower turns on but no flame. Blower runs for 10- 15 seconds and stops.
It is a Suburban Heater in a 2010 Heartland North Country. I don't have the model number handy right now.
Any suggestions? It is under Suburban Warranty, but I was wondering if there is something I can check before going that route.
Thanks in advance!
"If you remain calm while everything around you is chaos then you probably haven't fully understood the situation."
2006 Ford F-250, Crew Cab, Lariat, 6.0L Powerstroke
2010 North Country 27BHS
Me- Tommy
Wife- Lisa
Daughter- Makenna
Son- Kameran
|
JJBIRISH

Butler, PA, USA

Senior Member

Joined: 10/06/2002

View Profile


Good Sam RV Club Member
|
Restricted air flow can keep it from lighting…
Love my mass produced, entry level, built by Lazy American Workers, Hornet
|
ufda45

Alabama

New Member

Joined: 05/12/2011

View Profile


Good Sam RV Club Member
Offline
|
I had same experience this week, turns out that the oriface was clogged, not sure how that happened but had to remove the furnace and the oriface assembly and clean the small opening, runs fine now.
|
skipnchar

Topeka or somewhere else

Senior Member

Joined: 12/17/2003

View Profile

|
I"m assuming you mean it's your furnace not your water heater. When the blower runs it is measuring the air flow and when battery power is low the fan doesn't turn fast enough and it locks out. I know you said you're on shore power but how is your converter working? what voltage does your battery read? Battery voltage good on the battery means your converter is working OK and your problem is probably now low power. More likely a fouled burner or a number of other things that makes your furnace fail to light. Spark unit may be bad, soot in the burner, foreign matter in the LP feed line to the furnace are possibilities as is blocked exhaust in the furnace. At least gives you a place to start but the warranty shop would be where I'd take it on a new trailer. For what it's worth you should NEVER discharge your battery more than about 50% of you can very shortly kiss the battery good bye too.
Good luck / Skip
2011 F-150 HD Ecoboost 3.5 V6. 2550 payload, 17,100 GCVWR -
2004 F-150 HD (Traded after 80,000 towing miles)
2007 Rockwood 8314SS 34' travel trailer
US Govt survey shows three out of four people make up 75% of the total population
|
blksmith

Naches,WA

Full Member

Joined: 05/26/2008

View Profile

Offline
|
Here's what I had to do.
My furnace would start, no hot air, then would shut off.
Turn off the propane. Start the furnace. Let it run until it shuts down.Open the propane tanks and try your furnace again.Sometimes you have to purge the system of propane to prevent explosions.